We bought a new heater this season, a Raypak 206,000 BTU NG Electric Heater RHM-15-9962. It heated the pool nicely earlier in the week, but we turned it off when a cool spell was forecast. This morning I tried to turn it on and I get this error message: "Rollout SW Open". What does this mean? I appreciate the help.

JasonLion

0

TFP Expert

Platinum Supporter

LifeTime Supporter

May 7, 2007
37,770
Silver Spring, MD
  • May 18, 2013
  • Add bookmark
  • #2

Here is what I found in the manual: Roll Out Sw Open - Rollout Switch - verify gas pressure, combustion air, blocked heat exchanger, proper vent size/connections, high wind conditions.

ps0303

0

TFP Expert

In The Industry

Jul 6, 2011
4,177
FL
  • May 19, 2013
  • Add bookmark
  • #3

The rollout switch is activated when something like wind causes the flames to shoot out towards the front of the unit. This is usually caused by high winds while the unit is running. Are you sure it it said rollout? Sounds odd that you turn it on and the switch is open.

The rollout switch connects inside the cabinet right behind where the gas pipe comes into the gas valve. I have seen a few cases where the installer moved the rollout switch so they could install the gas pipe and they failed to put it back in place. This dangling switch is right by the burners then and when the units lights, its possible for the switch to trip open.

In any case this unit is under warranty. Hopefully your installer is also a warranty person for Raypak. Call them and have them come back and look at why the switch failed.

tlwilson

0

LifeTime Supporter

Aug 15, 2010
50
Nebraska
  • May 19, 2013
  • Add bookmark
  • #4

Thank you for your reply. It definitely says "Rollout SW Open". I will call the installer for the repair.

tlwilson

0

LifeTime Supporter

Aug 15, 2010
50
Nebraska
  • Jun 14, 2013
  • Add bookmark
  • #5

Our heater is still not fixed. They determined it wasn't getting enough gas so the gas company replaced our meter. Turned it on and the same thing happened. Now they say the wind diminished the flame and did something to the fireman's switch. Fireman's switch replaced and the wind keeps blowing out or diminishing the flame. Back and forth on how to protect it from the wind. Anybody with advice?

ps0303

0

TFP Expert

In The Industry

Jul 6, 2011
4,177
FL
  • Jun 15, 2013
  • Add bookmark
  • #6

The only thing you can do is add a wind stack to it. You've never had this issue before wind?

tlwilson

0

LifeTime Supporter

Aug 15, 2010
50
Nebraska
  • Jun 15, 2013
  • Add bookmark
  • #7

Our previous heater never had this problem. It was old and inefficient (still worked), but we wanted to upgrade. Raypak heater "Rollout SW Open" (8)

ps0303

0

TFP Expert

In The Industry

Jul 6, 2011
4,177
FL
  • Jun 15, 2013
  • Add bookmark
  • #8

Add the Raypak high wind stack. Probably $100 or around there.

tlwilson

0

LifeTime Supporter

Aug 15, 2010
50
Nebraska
  • Jun 15, 2013
  • Add bookmark
  • #9

Thanks for the help. I appreciate it!

B

[emailprotected]

0
Aug 26, 2014
1
Pensacola Florida
  • Aug 26, 2014
  • Add bookmark
  • #10

How did you solve the problem

Enjoying this content?

Support TFP with a donation.

Give Support

wjr75

0

LifeTime Supporter

Jun 6, 2013
898
IL
  • Aug 26, 2014
  • Add bookmark
  • #11

I wonder if you have a bad roll out switch. My old RP2100 heater had a wax one and I replaced it with a solid state one. It had a red reset button on it. That solved my roll out problem at the time. They also sell roll out switches that have different shutoff temps by about 10-15deg if I remember but you may not want to go there. I did buy one of the solid state versions which was higher but didn't need it.

J

Jayryght

0
Aug 19, 2016
11
Toronto, Canada
  • Aug 19, 2016
  • Add bookmark
  • #12

I have the same problem. Just happened to me today. I bought and got my heater installed in October 2013 and it heated the pool really nicely. I haven't used the heater in about a week. It's been really hot in Toronto. Today I wanted to do an evening swim with the kids and my wife so I thought I'd turn it on and had the "Rollout SW Opem" message. I thought it was a glitch so I cut the power to the unit and turned it back on, cut the gas and turned it back on, opened up the panel and cleaned any debris I could with a cloth rag and nothing. After reading the comments here I have located the switch but it does not have a reset button. I read somewhere that the newer models do not have one. Is it time to call for service or is there anything else I can do on my end? RSVP

Pool Clown

In The Industry

Sep 5, 2008
2,186
Silicon Valley, CA
  • Aug 20, 2016
  • Add bookmark
  • #13

If it is a Raypak heater, the roll out sensor is a one time use part, like a fuse, it isnt re-settable. I would replace it, leave the front cover removed, start the heater, and observe if the flame "rolls out". If you see this happen, turn off the heater immediately, and have a tech check the exchanger for sooting.

J

Jayryght

0
Aug 19, 2016
11
Toronto, Canada
  • Aug 20, 2016
  • Add bookmark
  • #14

Pool Clown said:

If it is a Raypak heater, the roll out sensor is a one time use part, like a fuse, it isnt re-settable. I would replace it, leave the front cover removed, start the heater, and observe if the flame "rolls out". If you see this happen, turn off the heater immediately, and have a tech check the exchanger for sooting.

I tried that. It doesn't even ignite. Nothing happens. It is just the error message.

wjr75

0

LifeTime Supporter

Jun 6, 2013
898
IL
  • Aug 20, 2016
  • Add bookmark
  • #15

You can jumper across the roll out sensor to see if it starts. This is just for testing purposes and shouldn't be left that way. Might have blown the replaced sensor again or may have some other board issue.

Pool Clown

In The Industry

Sep 5, 2008
2,186
Silicon Valley, CA
  • Aug 20, 2016
  • Add bookmark
  • #16

Jayryght said:

I tried that. It doesn't even ignite. Nothing happens. It is just the error message.

Did you replace the roll out sensor?
Trace the roll out sensors' wires all the way back to the board to make sure they haven't been chewed on.

J

Jayryght

0
Aug 19, 2016
11
Toronto, Canada
  • Aug 20, 2016
  • Add bookmark
  • #17

Re: Raypak heater "Rollout SW Open"

@wjr75 How do I do that? "Jumper across the rollout sensor?"

- - - Updated - - -

@pool clown: no I did not replace it. Not sure how to do that? I see the wires tracing up towards panel, but I guess I have to take off the panel to see it's source right?

- - - Updated - - -

@pool clown: no I did not replace it. Not sure how to do that? I see the wires tracing up towards panel, but I guess I have to take off the panel to see it's source right?

wjr75

0

LifeTime Supporter

Jun 6, 2013
898
IL
  • Aug 20, 2016
  • Add bookmark
  • #18

To jumper across you need a wire across the two terminals where the fuse (roll out sensor) is plugged into. If you do any electrical testing you usually have an alligator clip jumper wire which has one on both ends. But as said before this would be temporary.

J

Jayryght

0
Aug 19, 2016
11
Toronto, Canada
  • Aug 21, 2016
  • Add bookmark
  • #19

@wjr75 Thanks for the tip but I know verrrry little about electrical work and I don't even know what an alligator clip jumper wire is. At this point I may bite the bullet and call a tech. Kudos for your help though.

ps0303

0

TFP Expert

In The Industry

Jul 6, 2011
4,177
FL
  • Aug 22, 2016
  • Add bookmark
  • #20

Yes if you don't know much about electric or gas, call a tech and have them check it out.

Enjoying this content?

Support TFP with a donation.

Give Support

You must log in or register to reply here.

Raypak heater "Rollout SW Open" (2024)

FAQs

Why is my Raypak pool heater not heating? ›

Go make sure there aren't any tripped circuit breakers in the fuse box, then check that the unit's time clock is set to the “On” position. Check Filters & Strainers: Problems with slow or inefficient heating, as well as overly noisy operation, can sometimes be traced back to dirty filters and strainers.

Why does my pool heater spark but not light? ›

If you do have a spark, but the pilot doesn't light, a good bet is that you have a plugged pilot assembly or a bad gas valve.

Does water run through pool heater when heater is off? ›

Usually, there is a water bypass valve right at the heater's intake that allows water flow to go around the heater instead of through it. We don't need heat during the summers (and most other parts of the year in Florida), so water bypasses the heater most of the time.

What does "roll out switch open" mean? ›

The flame rollout switch is a safety feature that shuts off the gas supply to the burner if the flame blows out. This can happen for several reasons, such as a dirty burner or a blocked flue. A flame rollout can also be caused by a faulty gas valve or a problem with the electrical igniter.

What is a roll-out switch on a pool heater? ›

The rollout switch is activated when something like wind causes the flames to shoot out towards the front of the unit. This is usually caused by high winds while the unit is running.

How long should a Raypak pool heater last? ›

Often you need to replace a few essential parts, not the entire heater. Things like your climate, water chemistry, and maintenance habits will impact the lifespan of your pool heater. Pool heaters will last anywhere from 10 to 25 years.

Why is my pool heater not heating my pool? ›

Your heater may have inadequate water flow due to a dirty filter, closed valve, external bypass, reversed water connections, or pressure switch out of adjustment. It is also possible that your thermostat is out of calibration or needs to be replaced.

How do you reset a pool heater? ›

Reset your pool heater by flipping the breaker switch in the electrical panel to “off” and then “on.” Your breaker may be located in a disconnect box near your pool heater or in the breaker panel in your home.

Why is my water heater sparking but not lighting? ›

In many cases, the reason that you can't get your pilot light to ignite is that the pilot tube is clogged. This is a small metal tube that supplies the gas needed to ignite the pilot and keep it lit. The pilot tube often becomes clogged with debris, and this will prevent gas from flowing to the pilot light.

What causes ignition lockout on pool heater? ›

Clogged filters and strainers—unobstructed flow is required for proper temperature monitoring. High temperature setting—setting the pool heater to more than 105°F is an easy way to cause temperature excesses and lockouts.

Why does my pool heater say no water flow? ›

The most common reason for low or no flow is that the baskets are full of debris. By checking and emptying both the skimmer basket (by the pool) and the pump basket (inside the pump) will free up the water flow, allowing the system to fully 'prime' and function at full capacity.

What does the code if mean on a pool heater? ›

The IF code stands for ignition failure, which means your heater tried to light, but it did not. The SB code stands for a keypad failure. Pool and Spa Expert: Randy Huckstadt. The keypad failure is typically just the membrane pad.

Why does my pool heater say LP? ›

LP is an indication the low pressure switch is open. The switch opens when the refrigerant pressure drops below 80PSI, and will automatically reset at 120PSI.

What is open outlet water heater? ›

For open-outlet (low-pressure) storage type electric water heaters, they are designed to supply only one serving point and the outlet is controlled by a special water mixer which maintains a vented passage for the air inside the tank to the atmosphere.

References

Top Articles
Peugeot E-308 SW VS BMW 4er Gran Coupé Autovergleich | AUTOGOTT.AT
Peugeot E-308 SW VS Mercedes CLE Cabrio, Roadster Autovergleich | AUTOGOTT.DE
Consignment Shops Milford Ct
Gasbuddy Costco Hawthorne
Renfield Showtimes Near Amc Kent Station 14
Why Does It Say I Have 0 Followers on TikTok?
Palmbeachschools Jobs
Nbc4 Columbus Facebook
Www.citizen-Times.com Obituaries
Best Transmission Service Margate
How To Pay My Big Lots Credit Card
Delta Air Lines - Login
Large Pawn Shops Near Me
Gopher Hockey Forum
Craigslist Richmond Ba
Married At First Sight Novel Serenity And Zachary Chapter 950
Ihop Logopedia
Lebenszahl 8: Ihre wirkliche Bedeutung
Las mentiras y los crímenes que continúan. 9.11 X Veintitrés = Sin palabras
When Is Hobby Lobby Opening In Olean Ny
Fit 4 Life Murrayville Reviews
5162635626
Katonah Train Times
Brise Stocktwits
Cindie's - Lafayette Photos
Publix Store 1304
Forest | Definition, Ecology, Types, Trees, Examples, & Facts
Skip The Games Lawton Oklahoma
Craigslist Philly Free Stuff
Solid Red Light Litter Robot 4
How Much Does Costco Gas Cost Today? Snapshot of Prices Across the U.S. | CostContessa
Maine Marine Forecast Gyx
14314 County Road 15 Holiday City Oh
Walgreens Pharmacy On Jennings Station Road
Influencing Factors and Differences in Born Aggregometry in Specialized Hemostaseological Centers: Results of a Multicenter Laboratory Comparison
Publix Christmas Dinner 2022
Match The Criminal To The Weapon
Cnb Pittsburg Ks
Holley Gamble Funeral Home In Clinton
Probation中文
Watch ESPN - Stream Live Sports & ESPN Originals
Tattered Paws And Golden Hearts Rescue
The Safe Keeper Henderson
8 Common Things That are 7 Centimeters Long | Measuringly
7Ohp7
Chess Unblocked Games 66
Craigslist Ft Meyers
German American Bank Owenton Ky
Saulr80683
Sc4 Basketball
Sam Smith Lpsg
Latest Posts
Article information

Author: Sen. Ignacio Ratke

Last Updated:

Views: 6348

Rating: 4.6 / 5 (56 voted)

Reviews: 87% of readers found this page helpful

Author information

Name: Sen. Ignacio Ratke

Birthday: 1999-05-27

Address: Apt. 171 8116 Bailey Via, Roberthaven, GA 58289

Phone: +2585395768220

Job: Lead Liaison

Hobby: Lockpicking, LARPing, Lego building, Lapidary, Macrame, Book restoration, Bodybuilding

Introduction: My name is Sen. Ignacio Ratke, I am a adventurous, zealous, outstanding, agreeable, precious, excited, gifted person who loves writing and wants to share my knowledge and understanding with you.